The example D3 store building in the back for 2017 NEC does not mention anything about including a sign circuit in the description. But down below it adds it in.
600.5 says "each commercial building and each commercial occupancy accessible to pedestrians" so I guess I am wondering on the master electrician exam are they going to try and trick you like this. Or do you always add in the 1200VA x 125% for any store or commercial occupancy?