Re: store w/show window calculation
I see the basis of the 9,000 VA (3,000 square feet at 3 VA each). I see the basis of the 12,000 VA (200 VA per foot of show window times 60 feet).
Are you asking if the 5 receptacle outlets required by 210.62 (i.e., one per every 12 feet, along a 60 foot window) need to be counted as separate loads? If so, then my answer is ?No.? I believe the load associated with outlets to be installed above the window is accounted for in the show window calculation of 220.3(B)(7)(2).