You only need to worry about the space.. pipe is fine anywhere else.
 
Make up your mind....
Post 3 not above dedicated space. = no problem
Post 5 above dedicated space = problem IF, as infinity told you, its above the dedicated space above the equipment.
Example: 12" deep elecrtrical cabinet. mounted to the wall... IF the pipe is in that 12" envelope above the cabinet it must be addressed. if it's not as in 14" off the wall thus not over the cabinet, then ignore it.
 
It can't be in dedicated space.

If above dedicated space it could require drip pan or secondary containment of some sort if there is much risk for leakage or even risk of condensation to drip from it onto the electrical equipment.
 