STP for gas station

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have wiring going into sump pump located in tank concrete pad Class 1 Division 1 area. The sump pump is single phase 208V fed from 20A breaker has 2#12 conductors however their is no equipment grounding conductor provided. Does code require equipment grounding conductor for gas station sump pump?

Sent from my SM-G935U using Tapatalk
 
I have wiring going into sump pump located in tank concrete pad Class 1 Division 1 area. The sump pump is single phase 208V fed from 20A breaker has 2#12 conductors however their is no equipment grounding conductor provided. Does code require equipment grounding conductor for gas station sump pump?

Sent from my SM-G935U using Tapatalk

Yes, an equipment ground is necessary, and if the conduit is all metal, then it can serve that purpose.

Just an aside, it's a sub pump (submerged), not sump pump. Just sayin. :)
 