L Light Sabre Member Location Colorado Occupation Electrical Inspector Mar 28, 2025 #1 I am pretty sure, but cannot recall or find the article about having to use stranded wire for equipment that moves or vibrates… any input is much appreciated… GO!
I am pretty sure, but cannot recall or find the article about having to use stranded wire for equipment that moves or vibrates… any input is much appreciated… GO!
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Mar 29, 2025 #2 There is 410.56(E) but that for light fixtures on chain.
S suemarkp Senior Member Location Kent, WA Occupation Retired Engineer Mar 29, 2025 #3 610.11(C) for cranes, 675.4(A) for moving irrigation machines, 695.14(D) for engine driven fire pumps
610.11(C) for cranes, 675.4(A) for moving irrigation machines, 695.14(D) for engine driven fire pumps
Besoeker3 Senior Member Location UK Occupation Retired Electrical Engineer Mar 29, 2025 #4 FWIW we always used stranded for this kind of power electronics: https://imgur.com/o54m4If