System is 277/480 3phase. Lighting circuits are all 277 run through a Lutron relay panel. Circuits are individually controlled in sets of three by these relays. The devices are HID Low Bays. Breakers are 20 amp, relays are 16 amp cont load.
System has blown four Lutron Relays(rated 16A cont load). Previous techs found no anomolies(?). I tested and found all amps in range at 14 to 15.9 amps. Then I de-energized all units and re-energized single line. Amp rose to 18.8 for ten minutes. Then settled at 15.9amps. All circuits with 18 plus fixtures demonstrated same behavior. With shared hots on the circuit would go no higher than 15.9 amps. Is this EMF? Why do we only see the 18 amps with the other conductors de-energized?
System has blown four Lutron Relays(rated 16A cont load). Previous techs found no anomolies(?). I tested and found all amps in range at 14 to 15.9 amps. Then I de-energized all units and re-energized single line. Amp rose to 18.8 for ten minutes. Then settled at 15.9amps. All circuits with 18 plus fixtures demonstrated same behavior. With shared hots on the circuit would go no higher than 15.9 amps. Is this EMF? Why do we only see the 18 amps with the other conductors de-energized?