I got a call to check out some dimmers that were feeding stage lighting at a small bar. Six 500W PAR64's on two separate circuits controlled by two 1500W Lutron rotary dimmers. I did not remember to write down the dimmer part#, but if I had to guess, I would say they were between five to ten years old.
The lamps in the stage lights had been burning out every couple of months. Owner said they only used them on weekends for about a 4 to 6 hour stretch, which definitely seems like an abnormally short lamp life. He's been paying around $75.00 each for these lamps at the local music store, and so he wanted me to check out the wiring to see if I could find anything unusual that might be causing this.
All the wiring looked OK. The dimmers were located fairly close to the panel, so I was able to check every connection all the way back, and everything looked fine. The interior's of the fixtures looked OK - A couple of the fixtures had small signs of excess heat, but no outright browning or cracking of the fixture wire insulation. Line side of the dimmers read 121V hot to neutral, and nearly the same hot to ground. When I checked the load side, however, I read just over 90V hot to neutral, on both dimmers.
Is this normal? I'm pretty sure I've checked load side voltage on dimmers before and found normal 120V. I've always understood that dimmers work by "chopping" the voltage curve, rather than adjusting voltage.
Before I just assume the dimmers are the problem, and bill the customer for some high dollar replacement that may or may solve the problem, I figured I'd check in here to see if anyone had any thoughts.
One more thing I should mention. I had left my Fluke meter at another job, so I was checking voltage with a cheap Sperry meter. I think it is still a true RMS meter but not 100% sure.
The lamps in the stage lights had been burning out every couple of months. Owner said they only used them on weekends for about a 4 to 6 hour stretch, which definitely seems like an abnormally short lamp life. He's been paying around $75.00 each for these lamps at the local music store, and so he wanted me to check out the wiring to see if I could find anything unusual that might be causing this.
All the wiring looked OK. The dimmers were located fairly close to the panel, so I was able to check every connection all the way back, and everything looked fine. The interior's of the fixtures looked OK - A couple of the fixtures had small signs of excess heat, but no outright browning or cracking of the fixture wire insulation. Line side of the dimmers read 121V hot to neutral, and nearly the same hot to ground. When I checked the load side, however, I read just over 90V hot to neutral, on both dimmers.
Is this normal? I'm pretty sure I've checked load side voltage on dimmers before and found normal 120V. I've always understood that dimmers work by "chopping" the voltage curve, rather than adjusting voltage.
Before I just assume the dimmers are the problem, and bill the customer for some high dollar replacement that may or may solve the problem, I figured I'd check in here to see if anyone had any thoughts.
One more thing I should mention. I had left my Fluke meter at another job, so I was checking voltage with a cheap Sperry meter. I think it is still a true RMS meter but not 100% sure.