First post on here so excuse me if it’s in the wrong place.
Went to a house for a service call. Homeowner says lights are getting dimmer and brighter without any interaction with the switch.
I’m thinking, lost a neutral.
had power company come by and check at meter, no issues. Will be replacing service cable tomorrow after all the troubleshooting I did today.Short section between main breaker and meter. Maybe 8’ away. Btw older house so meter and panel aren’t back to back and it’s an older ite panel and 3wire system. SEU cable. Voltages would fluctuate from 230 on 1 leg and 10 on the other and many combinations in between. All adding up to approximately 240. Also noticed ground rod is not installed, not that that matters. I’m usually very good at trouble shooting but I was kinda stumped. It would only fluctuate from standard with 4 of the breakers in the whole panel.
Is it possible that it’s something else other than a dropped neutral between panel and EMC transformer? I’ve never seen anything downstream of service affect voltages in this way. Lower voltage yes but increased voltage I have not. Any help would be appreciated. Readings of voltage taken from lugs at main breaker panel.
Went to a house for a service call. Homeowner says lights are getting dimmer and brighter without any interaction with the switch.
I’m thinking, lost a neutral.
had power company come by and check at meter, no issues. Will be replacing service cable tomorrow after all the troubleshooting I did today.Short section between main breaker and meter. Maybe 8’ away. Btw older house so meter and panel aren’t back to back and it’s an older ite panel and 3wire system. SEU cable. Voltages would fluctuate from 230 on 1 leg and 10 on the other and many combinations in between. All adding up to approximately 240. Also noticed ground rod is not installed, not that that matters. I’m usually very good at trouble shooting but I was kinda stumped. It would only fluctuate from standard with 4 of the breakers in the whole panel.
Is it possible that it’s something else other than a dropped neutral between panel and EMC transformer? I’ve never seen anything downstream of service affect voltages in this way. Lower voltage yes but increased voltage I have not. Any help would be appreciated. Readings of voltage taken from lugs at main breaker panel.