Strapping emt

Status
Not open for further replies.

SAP

Senior Member
Location
Fresno Ca
We have a ground mount solar with 100 solar edge inverters, the underground is in pvc we are transitioning to emt it's about 2 feet from ground to inverter disconnect, since it is less then 3 feet do I have to strap (secure) my emt thanks
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
....would you stub a rigid conduit out of ground 24" , and thread a FS box onto it and call it good?
I would for the rigid(however, in that case the box itself would require a support), but for the OP it appears that the PVC/EMT transition is above grade and I would require a support for the EMT.
 