We have a ground mount solar with 100 solar edge inverters, the underground is in pvc we are transitioning to emt it's about 2 feet from ground to inverter disconnect, since it is less then 3 feet do I have to strap (secure) my emt thanks
EMT must be secured within 3' of termination point 358.30(A)
You're missing the OP's question. Does earth backfill count as "securement"?
....would you stub a rigid conduit out of ground 24" , and thread a FS box onto it and call it good?
I would for the rigid(however, in that case the box itself would require a support), but for the OP it appears that the PVC/EMT transition is above grade and I would require a support for the EMT.....would you stub a rigid conduit out of ground 24" , and thread a FS box onto it and call it good?