I have a receptacle right under my panel can I drop a homerun to it without strapping? It’s about 4-5 in below it
Is a plastic romex grommet considered a clamp? or does it need to be a metal squeeze connector?If there is a clamp securing it to both panel and outlet box I don't see why not. Each end requires securing within 12 inches, you have less than 12 inches between each clamp which is a securing method. Any inspector that wants to read between the lines here needs flogged, with a 4 foot piece of 12-2 NM cable.
If it is a 1 gang box with no clamps it needs secured within 8 inches. Clamp on the entry to panel is still securing it within 8 inches in OP's description.
What wording 334.30 allows the NM connect to support and secure the cable within 12" of the box or panel? I agree it's bogus but it's still required.If there is a clamp securing it to both panel and outlet box I don't see why not. Each end requires securing within 12 inches, you have less than 12 inches between each clamp which is a securing method. Any inspector that wants to read between the lines here needs flogged, with a 4 foot piece of 12-2 NM cable.
If it is a 1 gang box with no clamps it needs secured within 8 inches. Clamp on the entry to panel is still securing it within 8 inches in OP's description.
My assumption is that the panel was surface mounted but from the OP I guess that it could be recessed.
Some residential only guys don't know there are any other wiring methods besides NM and SE cable.If that's the case I'd highly recommend your suggestion made in Post #2.
JAP>
What wording prohibits it? There is no specific method of securing/support mentioned. Some places might have their own rules of what they acceptWhat wording 334.30 allows the NM connect to support and secure the cable within 12" of the box or panel? I agree it's bogus but it's still required.
Now those that insist there must be a completely separate support method within 12" from each end of the run will have their heads explode.Even if it is NM,,,, and the receptacle needs to be directly below the panel within 4 or 5 inches,,,, and you want to use materials you already have,,,, and the panel is surface mounted,,,, and your worried about strapping the NM,,,,, why not just butt the romex connectors together at the top of the receptacle box and bottom of the panel where there's no NM to be seen?
JAP>
I'd never do that on a loadcenter cover. Some commercial panelboards with a hinged cover may be a little more worth consideration in some situations, but still lean more toward no most of the time. If surface mounted I'd rather put something in the side vs the cover.Why not just mount the receptacle's box right to the panel cover? Chase nipple into the panel, and leave plenty of slack conductor to allow for removal of the cover.
View attachment 2551600
Now those that insist there must be a completely separate support method within 12" from each end of the run will have their heads explode.
Add: this is as stupid as those that think a 3 foot or less RMC nipple between two enclosures needs a strap on it.
Say one has two cabinets with a 3" RMC 3 feet long between them. You really think putting a strap on that is securing anything? Bet I can take a hammer to it and pretty much destroy the strap and will only put a few scratches in the RMC.
Why not just mount the receptacle's box right to the panel cover? Chase nipple into the panel, and leave plenty of slack conductor to allow for removal of the cover.