mphillipps
In a home, can stray voltage cause an excessively high power bill?
Two unit house. Circa 1950. Two separate electric meters. FPE breakers. One larger unit and one smaller unit. The smaller units electric bill is much larger (~ $100) than the large units bill. Small units tenant is seeking reimbursement for large power bill.
110826-1116 EDT
mphillipps:
Assuming a rotating disk kWh meter:
1. Turn every thing off in the house.
2. Disk should be perfectly still.
3. Turn one circuit on that has no load.
4. Disk should still be perfectly still.
5. Connect a 100 W 120 V incandescent bulb to the circuit. At 120 V this probably will be within +/-2% of 100 W.
6. Time exactly one revolution of the disk.
7. Determine the meter calibration constant, and calculate if it is working reasonably correctly based on the 100 W bulb load.
Assuming the meter is OK, then sell a TED 1000 series whole house monitor system to the customer. Then have the customer with your help analyze their consumption. You should order the in-line filter and Footprints software to go with the 1000 system. Note there are some problems if the customer is supplied from a three phase source.
Do not get a series 5000 system it possibly has major bug problems.
Drop by unannounced next week a couple times throughout the day and check the amperage on the two units. Betcha the smaller unit runs the A/C more. :happyyes:
This will take two people and maybe a couple radios.
Cell-phones?:lol: