Horses were shocked when they drank from the waterer. I'm thinking it's stray voltage. I disconnected the Hot,Neutral and Ground wires in the panel that feeds the waterer(This is the only thing on the circuit). I then checked for voltage at the waterer between the Hot and neutral, V=0, the Hot and Gnd, V=0 and the Neutral and Gnd, V=0. I then placed one lead of my meter into the earth and the other on the housing that the water bowl sits on (this is all metal) and it read V=.4. There is a ground rod at the waterer with a solid grounding wire attached to it and it connects to a lug on the metal housing. If I touch one end of my meter to the metal housing and the other to the waterer ground rod the reading is V=0. If I put one end of the meter in the earth any where else and the other to the metal housing my reading is V=.4. Just for kicks I went over to the Utility pole (about 20' away from the waterer), the transformer for the house sits on top of this pole and put 1 probe of my meter in the earth and the other on the Grounding wire that comes down the pole to a ground rod and the reading was V=.4.
1. What can I do to correct this problem so the horses can drink from the waterer with getting shocked?
2. Are there additional tests I can perform to help me troubleshoot this problem.
Thanks Jan
1. What can I do to correct this problem so the horses can drink from the waterer with getting shocked?
2. Are there additional tests I can perform to help me troubleshoot this problem.
Thanks Jan