I work for an electric co and we are investigating a report of stray voltage/shocks in an outdoor inground swimming pool. We measure 2.5 ? 3.0v from a metal ladder in the pool to a temp ground in the grass about 2 ft beyond the concrete walkway around the pool. Shutting off the power to the customer?s transformer, as well as the transformers feeding the neighbors on both sides, does not cause the voltage to disappear.
A neutral isolator/blocker is not an option, because when we cut the service neutral from the transformer, the stray voltage remained, apparently coming thru on the UG phone and/or tv cable system as well as thru our neutral.
Measurements from different ladders in the pool varied, with some as low as 0.5 or less to the same reference ground 2 ft off the concrete.
In the pool shed there is a sub-panel fed by 4 wires HHNG from the customer?s main panel at the house. If we disconnect the EGC that comes from the main panel from the grounding bus in the sub panel, which includes pool equipment grounds and the grounding grid around the pool, the stray voltage disappears completely.
What are the safety concerns if the EGC from the main panel is disconnected in the pool shed, separating the house grounds and the pool grounds? There is a possibility that the ground potentials between the house and the pool area could be different, but what scenarios other than lightning could introduce enough fault current into the ground to make this difference a danger to people? There are no high voltage electric lines either OH or UG anywhere near the pool area or closer than 200 ft from the house.
I understand there are exceptions allowed by the NEC where the EGC to a pool out-building is not required if the pool is built later. Is disconnecting the EGC in order to remove a stray voltage problem in a pool a valid exception? Any thoughts on this would be appreciated.
A neutral isolator/blocker is not an option, because when we cut the service neutral from the transformer, the stray voltage remained, apparently coming thru on the UG phone and/or tv cable system as well as thru our neutral.
Measurements from different ladders in the pool varied, with some as low as 0.5 or less to the same reference ground 2 ft off the concrete.
In the pool shed there is a sub-panel fed by 4 wires HHNG from the customer?s main panel at the house. If we disconnect the EGC that comes from the main panel from the grounding bus in the sub panel, which includes pool equipment grounds and the grounding grid around the pool, the stray voltage disappears completely.
What are the safety concerns if the EGC from the main panel is disconnected in the pool shed, separating the house grounds and the pool grounds? There is a possibility that the ground potentials between the house and the pool area could be different, but what scenarios other than lightning could introduce enough fault current into the ground to make this difference a danger to people? There are no high voltage electric lines either OH or UG anywhere near the pool area or closer than 200 ft from the house.
I understand there are exceptions allowed by the NEC where the EGC to a pool out-building is not required if the pool is built later. Is disconnecting the EGC in order to remove a stray voltage problem in a pool a valid exception? Any thoughts on this would be appreciated.