ken44
Senior Member
- Location
- Austin, TX
I just got back from trying to troubleshoot a problem that a customer was having at the electrical service of a recently purchased repossessed mobile home, they called me because lamps started blowing out when they went to turn on the switches. When I arrived I turned on power at the meter(200 amp service with the grounded conductor being grounded by means of a split bolt to the wire that was going up the pole to the transformer) and checked line and load voltages, everything was in order at the pole, however when I went to the panelboard, I found 230 volts from "A" phase to neutral explaining the burning lamp problem, at this point I had not turned the 200 amp breaker in the mobile home panel on yet, with it still off, I went outside to see the ground rod and wire, the person who did the work had put a plumbing fitting in line with the electrical PVC that had a hole in it and they ran the solid ground wire and the A/C wire out of that hole, then the ground wire was connected a ground rod sticking 16" out of the ground and clamped by means of a rubber hose clamp! I touched the rod and got a shock, there was 60 volts from the ground rod to the earth, I keep getting a continuity reading of zero ohms between one ground bar and the "A" phase wire and when I go to the other side of the ground bar to "A" phase with my ohmmeter, I get around 400 ohms. Alot of weird stuff going on, can anyone help. The panel in the mobile home is a 200 amp siemens panel. The service at the pole is a 200 amp GE and was done poorly by the utility company, they used 20' of EMT going up the pole, there are no screws in the meter box at all and only one screw in the GE can.