Stray voltage??

Status
Not open for further replies.

rhatch

Member
I was inspecting old barracks, and using a "current tester", I got readings (the tester started beeping) around the heat ducts (all you need to do is get close to an electrical flow to set it off). Last year our electrician checked out one of the barracks and couldn't find anything, but when I reinspected this spring....7 of the 8 barracks had readings. I checked around the furnace to see if there was a bad ground, or it was using the duct work as a ground..but that was inconclusive. Any thoughts??
 

Inspectorcliff

Senior Member
Location
Colorado
no path

no path

rhatch said:
I was inspecting old barracks, and using a "current tester", I got readings (the tester started beeping) around the heat ducts (all you need to do is get close to an electrical flow to set it off). Last year our electrician checked out one of the barracks and couldn't find anything, but when I reinspected this spring....7 of the 8 barracks had readings. I checked around the furnace to see if there was a bad ground, or it was using the duct work as a ground..but that was inconclusive. Any thoughts??

I have seen the only source of unbalanced current back to earth become dry and the electricity was seeking a path to earth and possibly the metal heaters were that path.

I once seen the old two screw in fuse panels glow red at night be cause the only source for the unbalance was through the grounding electrode conductor and it was either loose or the weather had been so dry and their was no path to earth.:confused:
 

wirebender

Senior Member
I don't know what is setting your tester off.

IMSO, if there is current on the duct and it is coming from the main power supply then there is a connection between a grounded conductor and the duct somehow. Or an ungrounded conductor and the duct is not grounded.

Whether or not there is a good path to ground is irrelevant since electricity does not try to return to ground it tries to return to source. If it is going to ground there is an unintentional connection somewhere. I would check all grounded conductor connections including at the service.

It may also be getting energized from the low voltage used for the A/C controls.
 

gndrod

Senior Member
Location
Ca and Wa
rhatch said:
I was inspecting old barracks, and using a "current tester", I got readings (the tester started beeping) around the heat ducts (all you need to do is get close to an electrical flow to set it off). Last year our electrician checked out one of the barracks and couldn't find anything, but when I reinspected this spring....7 of the 8 barracks had readings. I checked around the furnace to see if there was a bad ground, or it was using the duct work as a ground..but that was inconclusive. Any thoughts??

Hi Inspector rhatch,

There might be possible answers with a little more information. What type of current tester, what Amp readings resulted and type of raceway along side of ducting existed? You mentioned a beeping detector...sounds like a ticker or Voltage sensor. rbj
 

newenergy

Member
I can't remember where I saw it, but there's another thread, maybe on another forum about stray voltage at a military base that I think was caused by some sort of radar.
 