stray voltage

Status
Not open for further replies.

domnic

Senior Member
Occupation
Electrical Contractor
IF the power co would run neutrals or ground wires with their primary lines would this cut down on stray voltage in earth. does the power co use earth to help ground their system .
 

peter d

Senior Member
Location
New England
domnic said:
IF the power co would run neutrals or ground wires with their primary lines would this cut down on stray voltage in earth.

Stray current would be avoided if the utility did not use an MGN system (multi grounded neutral) and connected all of its transformers across two phase conductors.

domnic said:
does the power co use earth to help ground their system .

Yes, as I just mentioned the utility neutral is intentionally grounded at multiple points on their system. At high voltages the earth grounding is much more effective at fault clearing.
 

domnic

Senior Member
Occupation
Electrical Contractor
Mgn

Mgn

peter d said:
Stray current would be avoided if the utility did not use an MGN system (multi grounded neutral) and connected all of its transformers across two phase conductors.



Yes, as I just mentioned the utility neutral is intentionally grounded at multiple points on their system. At high voltages the earth grounding is much more effective at fault clearing.
what are multi grounded neutrals ?
 

peter d

Senior Member
Location
New England
domnic said:
what are multi grounded neutrals ?

The poco neutral is intentionally grounded/earthed at multiple points on the distribution system. This is done by ground rods and is required by the NESC for every pole that contains equipment (transformers, etc) as well as 4 connections to earth per mile.
 

mivey

Senior Member
peter d said:
The poco neutral is intentionally grounded/earthed at multiple points on the distribution system. This is done by ground rods and is required by the NESC for every pole that contains equipment (transformers, etc) as well as 4 connections to earth per mile.
Transformers but not all equipment.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
domnic said:
IF the power co would run neutrals or ground wires with their primary lines would this cut down on stray voltage in earth. does the power co use earth to help ground their system .
They do, and they do.

Stray earth currents are usually caused by poor or improper grounded-conductor connections.
 