Well good points made but i think most grounding issues are made by not testing your ground rods meaning it must be less than 5 ohms or lower and not the 25
Well good points made but i think most grounding issues are made by not testing your ground rods meaning it must be less than 5 ohms or lower and not the 25 ohms per nec thats not good enough i dont like the nec its not enough !
We have never checked ohms on a ground rod. Maybe I should start doing this. How do I test it?
We have always just sunk a 5/8" dia ground rod and run a #6 bare from it to the point in the meter can.
Well we test with old three point tester called a vibroground its a reed tester its better than the new clamp on testers . Most jobs we do the electrical engineer specs this type of tester ,also we must get per engineers request a 5 ohm or less resistance test on one rod . We also install a delta of 3 rods 40 foot down each cad welded rods 5/8 copper clad and attach a 3/0 copper cad welded gec we also have these rods 30 foot apart in a delta arrangement to each other rod . we test each rod one at a time then we test the whole complete system when finished . We get less than one ohm every time and must have a engineer witness the test with inspector on site . we do this on every job . My reason for 5 ohms or less is what i have been doing for years and on every job its required ? comments ?best to ya
Well we test with old three point tester called a vibroground its a reed tester its better than the new clamp on testers . Most jobs we do the electrical engineer specs this type of tester ,also we must get per engineers request a 5 ohm or less resistance test on one rod . We also install a delta of 3 rods 40 foot down each cad welded rods 5/8 copper clad and attach a 3/0 copper cad welded gec we also have these rods 30 foot apart in a delta arrangement to each other rod . we test each rod one at a time then we test the whole complete system when finished . We get less than one ohm every time and must have a engineer witness the test with inspector on site . we do this on every job . My reason for 5 ohms or less is what i have been doing for years and on every job its required ? comments ?best to ya
What are the soil conditions where you achieve 1 ohm? Just curious.
I've done tests in clay and could'nt achieve 1 ohm. Then again that
was in 80's. Our meters were'nt as sophisticated as they are today.
Well I am one of those telecom engineers that specify 5 ohm grounds, and it has nothing to do with stray voltage. In fact the lower the ground electrode impedance is, the higher your stray voltages will be because of more current flow via earth. Further the NEC does not require a 25 ohm ground period.Well good points made but i think most grounding issues are made by not testing your ground rods meaning it must be less than 5 ohms or lower and not the 25 ohms per nec thats not good enough i dont like the nec its not enough
Well we disagree with the comments on the 25 ohms . Read article 250.56 a single electrode consisting of a rod pipe or plate that does not have a resistance to ground of 25 ohms or less shall be augmented by one additional electrode ect ect .