We are doing a job where the strip store is breaking through the fire walls to expand their store from the other strip store next door. My question is: Since there is now 2 services in 2 different locations are we required to have all the disconnects in one location by installing a disconnect and running subfeed cable to one of the services or can we just put a plaque on one of the services stating where the other service is located????
 
We are doing a job where the strip store is breaking through the fire walls to expand their store from the other strip store next door. My question is: Since there is now 2 services in 2 different locations are we required to have all the disconnects in one location by installing a disconnect and running subfeed cable to one of the services or can we just put a plaque on one of the services stating where the other service is located????


You'll need to relocate the disco to where the other one is. The only reason it was originally allowed to be in a different location was because the fire wall.
 
We are doing a job where the strip store is breaking through the fire walls to expand their store from the other strip store next door. My question is: Since there is now 2 services in 2 different locations are we required to have all the disconnects in one location by installing a disconnect and running subfeed cable to one of the services or can we just put a plaque on one of the services stating where the other service is located????

Can you meet one of the conditions listed in 230.2(A),(B),or(C)?

You might be able to get special permission for the AHJ to have 2 services on the building.

If you can get the permission then you would have to identify the services in accordance with 230.2(E).

Chris
 