Is it ok to strip outer casing of mc cable and slide it down a piece of EMT? I have a j box up in the attic with EMT running down the wall.
I realize some think the individual conductors are required to be marked, but that is not what is actually required. As long as the MC cable is marked as required, the jacket-stripped-off conductors are not required to be otherwise marked.Besides the proper transition fitting, do the stripped MC conductors comply with 310.120, 2011 NEC?
310.120 Marking.
(A) Required Information. All conductors and cables
shall be marked to indicate the following information, using
the applicable method described in 310.120(B):
(1) The maximum rated voltage.
(2) The proper type letter or letters for the type of wire or
cable as specified elsewhere in this Code.
(3) The manufacturer?s name, trademark, or other distinctive
marking by which the organization responsible for
the product can be readily identified.
(4) The AWG size or circular mil area.