So I need some help with Thermal Mag breakers
NEC 430.25 states that a thermal mag should be sized to 250% of FLA.
How does the adjustable magnetic setting come into this to meet code?
My motor FLA is 144A with a 300A ITE JL type breaker. The setting is turned all the way up and creates a conflict with coordination on the upstream switch rack.
Thanks