Stub up in footings

CubpME52

Member
Location
Texas
Occupation
Electrician
Has anyone stubbed up through a building footing or building column footing. On a project where they are allowing it. I've always been told to stay away from them
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I don't see it as a problem as long as it is approved by the structural engineer.
I agree. If the engineer approves it I wouldn't worry about it. It's not the sparkys job to decide if the conduit will result in a structural defect.
 

Seven-Delta-FortyOne

Goin’ Down In Flames........
Location
Humboldt
Occupation
EC and GC
Any slab on grade will have conduits and dwv piping through the footing.

Ive brought them up through footings before.

I would avoid column footings though. Not sure if that’s a code issue.
 