NSmithIN
- Valparaiso, IN
What is the recommended center to center spacing for qty. (3) 4" rigid PVC conduits. The conduits will be embedded in concrete slab for a bottom entry into an 800A panelboard
How do you like that Eaton gear?
sokay... this is the second job i've used the stuff on... first job had a dozen
3R panels, and 1,200 amp gear, and the stuff is pretty well finished, and
not expensive beyond all reason... my wholesale house sells a lot of it.
i can't find any fault with it to speak of.
I'm only asking because I'm current installing 3-4000 amp services with all Eaton equipment and putting the bus links in between the sections isn't fun. :roll:
I do agree that it's pretty nice stuff but with a few caveats.
had to pull the guts out the top of the gear and tuck them in the conex
until after the wire is pulled and laced.. there isn't much room between the
bottom of the buss, and the slab. it's cozy, and i packed too many marshmallows
in the piggy bank. it's a 1,200 amp buss, with an adjustable main.
specs called for 800 amps of 480, with provision for expansion, so i bumped everything to
1,200 amp, and it's fed off a 800 amp breaker in the metering section nearby,
that has a 1,200 amp case with 800 amp trip, and 1,200 amp vertical buss on
2,000 amp horizontal bus, so upgrading is just changing out the trip unit.