Which values am I taking from this HVAC unit for my calculated load? It will be run on a single phase 120/240 volt system. The compressor motor is rated for 230 volts. My drafters/engineers are adamant about using 230 instead of 240 volts.
1. To get my VA for the total calculated load for my feeders, would I use the FLA from the heater package? Or the RLA from the electrical ratings?
2. Since the unit is operating on 240 real world volts, I should use 240 for my calculation, correct?