Interesting....out west, I think we're just the opposite. Metering is ahead of any disconnects unless more than 6 service disconnects (per Code) The reason we don't allow it is that we don't want a customer to have access to unmetered conductors, but also because meters are powered by the line voltages, and shutting off the disconnect ahead of metering would cause the meter to stop transmitting data, causing a "No Report" condition, which requires a visit by the metering dept. Also, even on a disconnected service (we lock the service disconnect off on CT services), we like the meter to stay energized so that we can verify every month (remotely) that there has been no usage.