A quick question on the size of the conductors that feed a sub-panel. I understand the sizing of the conductors is based on the calculated load. The protection of the conductors is per the OCPD that the condcutors attach to and I also understand that the rating of the panel cannot be less than the OCPD. With all of this, does 240.4B (next breaker up) apply to these conductors when you dont know the actual load that the panel serves?
Example: I have a 200 amp panel in a strip mall. No idea what this panel may some day serve since the retail space is empty. I size the conductors off of the 200 amp OPCD at the meter, so 250 kcmil XHHW aluminum is installed, rated at 205 amps since the terminations of the breaker is 75 degrees. My comepetition at another suite installs 4/0 aluminum rated at 180 amps, applies 240.4B, next breaker size up is a 200 amp OPCD.
This seems logical since the panel shouldn't be loaded past 80%, but who really checks the panel loading when there could be a number of EC's (and possibly non-electricians) adding loads to this panel?
Should I assume that you can pretty much always install "the next size wire under" the breaker (commercial applications) except for the exceptions listed in 240.4B?
Mike
Example: I have a 200 amp panel in a strip mall. No idea what this panel may some day serve since the retail space is empty. I size the conductors off of the 200 amp OPCD at the meter, so 250 kcmil XHHW aluminum is installed, rated at 205 amps since the terminations of the breaker is 75 degrees. My comepetition at another suite installs 4/0 aluminum rated at 180 amps, applies 240.4B, next breaker size up is a 200 amp OPCD.
This seems logical since the panel shouldn't be loaded past 80%, but who really checks the panel loading when there could be a number of EC's (and possibly non-electricians) adding loads to this panel?
Should I assume that you can pretty much always install "the next size wire under" the breaker (commercial applications) except for the exceptions listed in 240.4B?