sub-panel disconnect
derease
I ran a sub-panel to a garage that is 25 feet from the main residence. It is a 100 amp sub-panel with 16 spaces. It is a lug panel with the main breaker in the residence at the main panel. my question is do I need a disconnect (main breaker) in the sub-panel? I already missed having a grounding rod for the sub and don't want to miss anything else. Any advise would be appreciated. Thanks Dave
augie47
Tennessee
How many breakers are being installed in the sub-panel ?
If more than 6, you need a main in the panel.
The sub panel must comply with 225.21 nad 225.36
charlie b
Seattle, WA
Electrical Engineer
To be more precise, there must be a way to disconnect all power from the garage, and it has to be local to the garage. The breaker in the house panel will not suffice. The easiest way to achieve this is to have a main breaker in the garage panel. But that is not the only way. A non-fused disconnect outside the garage is another option.
Dennis Alwon
Chapel Hill, NC
Retired Electrical Contractor
Dave, be careful if you use a MLO panel and install a main breaker then you will have to use a retainer clip for the main.
408.36(D) Back-Fed Devices. Plug-in-type overcurrent protection devices or plug-in type main lug assemblies that are backfed and used to terminate field-installed ungrounded supply conductors shall be secured in place by an additional fastener that requires other than a pull to release the device from the mounting means on the panel.
derease
There is a square d panel in the garage (lug panel). Can I just add a 100 amp breaker inside the panel to feel the bus bars?
augie47
Tennessee
You can. If you are using a branch breaker spot be sure to heed Dennis' advice on the retainer clip.
haskindm
Maryland
I many areas, if the panel has the capacity for more than six breakers a disconnect will be required. Any other words, if I only install 4 breakers in a 40-circuit panel, the AHJ in this area would require a disconnect. If I install a 6-circuit panel, they would accept it and no additional disconnect would be required.
roger
Fl
What do these inspectors do if you have to supply a load requiring 70 amps with a fusible disconnect?
Roger
roger
Fl
To the wire, did you run 3 conductor with ground? If you did I believe there is no need for a ground rod.
The GES is required, read 250.32 taking note of the first sentence of 250.32(A)
Roger
Dennis Alwon
Chapel Hill, NC
So you install a six circuit panel or 12 circuit panel--- suppose I want 6 DP breakers as my disco. Here's the problem. I install 4 dp and have space left for 2 more DP or 4 sp---- then what do you do. :)
LarryFine
Henrico County, VA
Nothing; it's not my issue.
What, me worry?
LarryFine
Henrico County, VA
. . . im not understanding why i cant just run a 4-wire and no groundrod at the garage
Because, unless the supply is a circuit (single or MWBC), the separate structure is required to hane an electrode system.
In a nutshell, a separate structure fed by a feeder is wired like a service as far as grounding is concerned, and like a sub-panel as far as bonding is concenred.