I have a 120/208V sub panel in a very small switchgear building that has a panelboard with 24 circuits (only 4 ckts are being used for lights and receptacles)
It is not an occupancy or dwelling unit. It’s located an industrial plant.
The panel is fed off a branch circuit from a panelboard in another building approximately 150 feet away.
the sub panel does not have main circuit breaker? Is MLO ok ?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
the sub panel does not have main circuit breaker? Is MLO ok ?
Other issues aside, no, there should be a disco outside or inside nearest the point of entry.

That's because it comes from another building, not another panel.
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Other issues aside, no, there should be a disco outside or inside nearest the point of entry.

That's because it comes from another building, not another panel.

Exceptions? The branch CB from the main panel is lockable


Sent from my iPhone using Tapatalk
 
Last edited:

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Other issues aside, no, there should be a disco outside or inside nearest the point of entry.

That's because it comes from another building, not another panel.

Also only 4 CBs are being used - allowed up to six for a service.


Sent from my iPhone using Tapatalk
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Also only 4 CBs are being used - allowed up to six for a service.
Okay, I missed that, unless the 6-handles-in-one-enclosure allowance has gone away.

However, the entrance location requirement still applies, if I'm not mistaken.
 