I’m planning to upgrade the service in a detached garage, which is currently fed by a single 15amp circuit, and I wanted to confirm that I have my circuit sizing correct. The existing circuit runs through ¾” IMC buried under the driveway, which I’d like to re-use to run a new feeder circuit to a sub-panel in the garage. Per Table C.1, I can have a maximum number of 4 conductors for 6AWG THWN-2, Table 310.15(B).16, says I can run a maximum of 75amps on 6AWG copper THWN-2, and 310.15(B) states that I do not need to de-rate for 3 or fewer conductors. The rest of the circuit (main load center to buried conduit, then from buried conduit to the sub panel) will be run though 1” PVC conduit. Based on this, I believe I should be able to run a 70 amp breaker for this circuit. Am I correct on the sizing, or am I missing anything?