70A breaker in main panel protects a 125A MLO sub-panel. Size the feeder for 70A or 125? Thanks
G Gshell82 Member Location Boston May 31, 2018 #1 70A breaker in main panel protects a 125A MLO sub-panel. Size the feeder for 70A or 125? Thanks
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician May 31, 2018 #2 The ampacity of the sub-panel is irrelevant as long as it's greater than or equal to the feeder size which is 70 amps due to the OCPD ahead of it.
The ampacity of the sub-panel is irrelevant as long as it's greater than or equal to the feeder size which is 70 amps due to the OCPD ahead of it.
kwired Electron manager Location NE Nebraska Jun 1, 2018 #3 What he said - plus do a load calculation for what you will have for loads. You should only match your gear and conductors to what you have when it is more then what load calculation says is the minimum. If you came up with a calculation of 137 amps - neither the 70 amp breaker or the 125 amp panel really do you any good.
What he said - plus do a load calculation for what you will have for loads. You should only match your gear and conductors to what you have when it is more then what load calculation says is the minimum. If you came up with a calculation of 137 amps - neither the 70 amp breaker or the 125 amp panel really do you any good.
publicgood Senior Member Location WI, USA Jun 2, 2018 #4 As kwired said, follow the code and do a calculation to properly size the feeder. Consider the continuous and non, also demand factors.
As kwired said, follow the code and do a calculation to properly size the feeder. Consider the continuous and non, also demand factors.
publicgood Senior Member Location WI, USA Jun 2, 2018 #5 publicgood said: As kwired said, follow the code and do a calculation to properly size the feeder. Consider the continuous and non, also demand factors. Click to expand... If 70A meets the code load calc, 70A and not 125A would be the feeder.
publicgood said: As kwired said, follow the code and do a calculation to properly size the feeder. Consider the continuous and non, also demand factors. Click to expand... If 70A meets the code load calc, 70A and not 125A would be the feeder.