Re: sub panel for media room
Keep in mind you cannot totally isolate this panelboard from the rest of your systems. It still has to be connected to your home's grounding system (usually the ground bar in the main panel), that all the other grounds are connected to.
If you run romex from the main panel to the subpanel and then use all plastic boxes as another poster suggested, you will have the best "isolation" you can get.
Route the new cables as far away from any sources of electrical noise and whatever feeds those sources (motors, dimmers, flourescent fixtures, etc) as is practical.
You might be tempted to put the whole thing in metal conduit to reduce noise even farther, but in reality metal conduit is not an effective high frequency shield and may actually act as an antenna, more so then Romex would.
You may also want to consider adding a whole house transient suppresser. The suppresser should be installed at your service panel by someone qualifed to do so. this will give you fairly good protection against electrical transients entering your home. You should probably forget adding power strip type protectors as they are generally not especially effective.
You may want to try adding an RFI filter to the power feeding your equipment, as its just as likely "noise" is coming in on the power wires as it is on the ground wire. this is something you might want to experiment with to see if it improves anything.
lastly, consider this. many times problems are blamed on "bad" grounds that are really caused by other issues such as poor equipment design or long lead length.
[ October 27, 2004, 10:37 AM: Message edited by: petersonra ]