Maintenance guy in factory here just trying to learn.
We have a 480v panel that supplies a 25kva transformer. Single phase 480v primary, 240/120 secondary. The neutral of the transformer is not bonded to the case or ground. There are two panels getting power from this transformer, one has a main breaker (100A) and the other, a GE load center has a backfed (60A) breaker. Both of these panels have the grounds and neutrals together and the panel with the main has the neutral/ground bar still in it. Both panels are for additional office space.
I know if this were my house and i was installing a sub panel this would be wrong. Remove the ground/neutral bar as to not provide a parallel path. Is this ok or not?
Thanks
We have a 480v panel that supplies a 25kva transformer. Single phase 480v primary, 240/120 secondary. The neutral of the transformer is not bonded to the case or ground. There are two panels getting power from this transformer, one has a main breaker (100A) and the other, a GE load center has a backfed (60A) breaker. Both of these panels have the grounds and neutrals together and the panel with the main has the neutral/ground bar still in it. Both panels are for additional office space.
I know if this were my house and i was installing a sub panel this would be wrong. Remove the ground/neutral bar as to not provide a parallel path. Is this ok or not?