Looking at a small job for an emissions testing station. Located at what once was a hand car wash at a service station. So it's separate building with a sub panel and no equipment ground ran at the time of install.
Probably be very hard to install a ground conductor at this point and the building is old enough for it to be legal at the time of original install.
After looking a 2017 NEC article 250.32 (B) (1) Exception # 1 the code indicates that it's legal to leave as is. I didn't notice any metal connections between the buildings such as a water pipe.
Any thoughts.
Probably be very hard to install a ground conductor at this point and the building is old enough for it to be legal at the time of original install.
After looking a 2017 NEC article 250.32 (B) (1) Exception # 1 the code indicates that it's legal to leave as is. I didn't notice any metal connections between the buildings such as a water pipe.