Re: Sub Panel in Closet?
Strictly speaking the closet thing is open to interpretation by the AHJ. If the contents are considered combustibles the panel can't be there. A workaround may be to divide the closet and provide a clear section for the panel. Check with your AHJ. Look at 240.24(D)(E) about closets & bathroom panels. The rest of your question is answered by Article 110 and the way your AHJ interprets it. There is a lot of important stuff in 110 about how your subpanel needs to be.
Multi-Wire branch circuits must be on separate phases. They are also called Edison Circuits if the circuits land on one yoke or strap. Look at Article 100 for details. Also, look at 210.4(A), 210.4(B), 210.7(C), 240.20(B)(2), and 300-13(B) in the 2002 NEC for more details. Also, check with your AHJ to see if multi-wire circuits must originate from adjacent breakers, or if they require a handle-tie. If they land on one yoke or strap they do need a handle-tie-- the rest is up to the AHJ.
If you post back with more detail we can provide you with a less generic, and a better & safer answer.
How far does your experience go back? What is your experience?