Sub panel in commercial bathroom

Status
Not open for further replies.

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
1. Can you put a service panel or sub panel in commercial bathroom with proper working space? I see it’s prohibited residential via 240.24.


2. If commercial panel is existing in commercial bathroom can you run new circuits to that panel?

My opinion is yes to both in 2017 NEC I greatly appreciate input
 

rc/retired

Senior Member
Location
Bellvue, Colorado
Occupation
Master Electrician/Inspector retired
A service disconnect can't be installed in a bathroom. 230.70(A)(2).
Yes, you can install a sub panel in a commercial bathroom.
Yes, you can add circuits to an existing sub panel in a commercial bathroom.

Ron
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
A service disconnect can't be installed in a bathroom. 230.70(A)(2).
Yes, you can install a sub panel in a commercial bathroom.
Yes, you can add circuits to an existing sub panel in a commercial bathroom.

Ron
Thank you
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
A service disconnect can't be installed in a bathroom. 230.70(A)(2).
Yes, you can install a sub panel in a commercial bathroom.
Yes, you can add circuits to an existing sub panel in a commercial bathroom.

Ron
Also thank you for the reference
 
Status
Not open for further replies.