Actually, I don't see any code that forbids that.Originally posted by diggers:
I disagree with this also as it may be used in the future for a 120V circuit somewere.
We don't know that. You interpreted the "3-wire feeder" to mean that the neutral wire is being used as both a neutral and an EGC. That would be forbidden, as you pointed out.Originally posted by peter d: It's not allowable, and the code that forbids this is 250.142(B)
Sounds OK to me.NO-NO, I mean 2-current carriers and 1-ground in pvc to a sub without a nuetral.
Does 250.142(B) require a neutral to a sub-panel?Then you are definitely violating 250.142(B)
He intends to feed only 2 a.c. units (4-8 space panel), but, if the a.c. units are removed or what have you, then you will have an improper sub panel for 120v/240v. And we all know someone will come along and use it for 120/240.How about this one:
He says he will also run only 3-wire to a sub panel if it only feeds 220V circuits.
I disagree with this also as it may be used in the future for a 120V circuit somewere.
If we have line-to-neutral loads, we need a grounded conductor. 250.142(B) forbids us from using the grounded conductor for equipement grounding. Therefore, we must run an EGC for a "sub panel"Originally posted by infinity:
Does 250.142(B) require a neutral to a sub-panel?
I just installed such a system in a warehouse, aq 120' run, where only the outside AC unit and inside air handler w/strip heat are fed. The advantage is that there is a #2 al SE cable that has a maximum load of 48 amps at any given moment, for lower voltage drop.Originally posted by diggers:
He intends to feed only 2 a.c. units (4-8 space panel), but, if the a.c. units are removed or what have you, then you will have an improper sub panel for 120v/240v. And we all know someone will come along and use it for 120/240.
Not for a while. Read 250.134 through 250.142Originally posted by peter d:
There are exceptions to this rule . . . of course the 3-wire dryer and range circuits.
I'm aware of that. I was just making the point that they are one of the very few examples where the grounded conductor is permitted to serve as the EGC also, as long as the it's an exsisting installation acoording to 250.142(B)Exception 1.Originally posted by LarryFine:
Not for a while. Read 250.134 through 250.142