Through the ground screw away.
The panel is listed for the purpose. To remove the bonding jumper and use one of the bars as a ground bar rather than a neutral violates the listing.
james wuebker said:It could make the panel confusing to some.
Jim
I agree with you as long as things are labeled inside.infinity said:That seems like the biggest issue. Someone will eventually land some neutrals on the ground bus. IMO the $5 ground bar kit is a better job but I agree with Raider that it can be done without violating the listing. We occasionally use GE panelboards and I've noticed the note he mentioned.
This provides a means for the installer not to place 2
grounded conductors under 1 screw in violation of NEC.
Could someone save me the trouble and give me the NEC section that prohibits placing 2 grounded conductors under 1 screw?
hardworkingstiff said:Good info. I never knew you could remove the jumper neutral bar and still have UL listing.
Could someone save me the trouble and give me the NEC section that prohibits placing 2 grounded conductors under 1 screw?
Thanks,
Lou
raider1 said:Please provide the listing that says that it can't be used as a grounding bar.
Here is a quote from the installation instructions for a GE PowerMark Gold Load Center.
"The neutral crossbar may be removed to provide optional neutral and ground wiring as follows:"
It goes on to show a table that allows the terminals on the right or left side of the panel can be used for neutral or ground.
Chris
Paul B said:I would like to see that section also.