I'm istalling a 100 amp sub-panel into a garage about 100' away. I got #2 aluminum wire, do I have to use the same size ground wire? If not what size do i need?
* This NEC? Forum is for those in the electrical and related industries.
Questions of a "How-To" nature by persons not involved in the electrical industry will be removed without notice.
Please read our rules and disclaimers.
The garage is not a dwelling.(6) 120/240-Volt, 3-Wire, Single-Phase Dwelling Services and Feeders For individual dwelling units of one family, two-family, and multifamily dwellings, conductors, as listed in Table 310.15(B)(6), shall be permitted as 120/240-volt, 3-wire, single-phase service-entrance conductors, service lateral conductors, and feeder conductors that serve as the main power feeder to each dwelling unit and are installed in raceway or cable with or without an equipment grounding conductor. For application of this section, the main power feeder shall be the feeder(s) between the main disconnect and the lighting and appliance branch-circuit panelboards(s)
A panel that not as high up on the chain of command as the main panel.What's a "sub panel?"
i thought it was a panel that was underground, " sub terranean panel".Originally posted by hurk27:
A panel that not as high up on the chain of command as the main panel.What's a "sub panel?"
#2 is not a wire size recognized by the NEC.Originally posted by marlboro12:
I'm istalling a 100 amp sub-panel into a garage about 100' away. I got #2 aluminum wire, do I have to use the same size ground wire? If not what size do i need?
Tom, why would you say that #2 is not recognized by the NEC. It appears twice in table 250.66 alone.#2 is not a wire size recognized by the NEC.