Michael White
Member
- Location
- Apache Junction Arizona
I installed a sub panel in a detached garage fed from a 50a breaker in main house panel. It was approved as a main lug only by Peoria Az. plan review. When it was inspected the inspector said that since it contained more than 6 breakers it was required to have a main breaker. I stated that the rule only applied to services, not sub panels. He said that since you couldn't see it from the main panel it needed the main. To avoid further argument I replaced the panel with a 100a with main breaker. Now he says that the main must be 50a max, so that it wouldn't overload the 50a feeders. I stated that the main was only being used as a switch and since the feeders were already protected at 50a it was impossible to overload the feeders with a downstream 100a. He is adamant that I have to change the main, does he have any grounds for this ruling.