stew
Senior Member
- Location
- federal way,washington
when is a main breaker required in a subpanel?
suemarkp said:Doesn't 225.33(A) and 408.36(A) Exception 1 answer most of your issues.
Yes and no. Don't confuse the requirements for access to the service disconnect and the OCP device.buck33k said:In reading 230.92 it seems in the above case the downstream OCP would have to be of a lesser rating, for instance if the locked service disconnect for an apartment were 80 amps, the panel main would have to be 70 amps. Am I on the right track?
LarryFine said:Yes, but it does not allow locked/inaccessible disconnects, only OCP devices.
Doesn't locking out an occupant interfere with "readily accessible"?230.70(A)(1) Readily Accessible Location. The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors.
LarryFine said:Doesn't locking out an occupant interfere with "readily accessible"?
LarryFine said:Doesn't locking out an occupant interfere with "readily accessible"?
LarryFine said:Why not? The occupant has that access.
That home or business with the indoor disconnect certainly has access by the occupant.iwire said:If it does than no home or business could have an indoor service disconect.
That's not the same as a single-occupancy premises.iwire said:Does the tenant in a apartment building ave access to the main?[/i]
Same response, and often not.Does the tenant in an office building have access to the main?
Are they supposed to have ready access to disconnects? If so, then no indoor disconnects would be allowed, as you stated.Does the fire dept have keys to everyones home.
I am not sure which code section you are saying prohibits looked doors?