My question is for a sub panel located "Within the same building" as the main disconnect. I just want to know the code requirement for not needing to have a main in the sub panel
 
My question is for a sub panel located "Within the same building" as the main disconnect. I just want to know the code requirement for not needing to have a main in the sub panel
...
408.36 Overcurrent Protection. In addition to the requirement of 408.30, a panelboard shall be protected by an overcurrent protective device having a rating not greater than that of the panelboard. This overcurrent protective device shall be located within or at any point on the supply side of the panelboard.
 