Regarding sub-panels, I'm looking for code references that talk about whether the sub panel needs to be a MLO or a Main Breaker?
I know typically a sub is protected at its source by a breaker sized to protect the feeder that feeds the sub. Also I know the sub is sized for the load of the ckts that originate from it, which is used to decide the feeder size (125% of continuous + 100% non-continuous).
What code reference tells me if/when it's necessary to have a main breaker in the sub?
I would assume it's related to treating the main breaker in the sub as a disconnect, because the feeder is already protected. So, if you need to do work on the branch circuits you can disconnect power at the sub (example, re-arrange breakers to add or delete ckts, etc) rather than go all the way back to the main panel to disconnect power to the sub.
So maybe a matter of convenience? Maybe it's a design issue that the code doesn't specifically address? Or am I missing something?
Thanks for feedback!
I know typically a sub is protected at its source by a breaker sized to protect the feeder that feeds the sub. Also I know the sub is sized for the load of the ckts that originate from it, which is used to decide the feeder size (125% of continuous + 100% non-continuous).
What code reference tells me if/when it's necessary to have a main breaker in the sub?
I would assume it's related to treating the main breaker in the sub as a disconnect, because the feeder is already protected. So, if you need to do work on the branch circuits you can disconnect power at the sub (example, re-arrange breakers to add or delete ckts, etc) rather than go all the way back to the main panel to disconnect power to the sub.
So maybe a matter of convenience? Maybe it's a design issue that the code doesn't specifically address? Or am I missing something?
Thanks for feedback!