I too do not understand your 12" wide comment. I am inclined to say that if coming up a set of steps to an area that is 3' x 3', then on up one direction or another, go for it. No part of your 30" working width being over a riser.
Disclaimer: I am not your AHJ.
Like I said I don’t understand where the 12” comes into play. My point would be that I would not consider a 3x3 area, steps.A 3'x3' landing at the top of a set of steps than one step up (12" wide) in another direction?
-Hal
I think I understand why she wants it on the step, probably something along the lines of being more visually aesthetic to a long hallway, but your the professional just tell her code requires having 3 ft of solid footing below the panel for servicing stability. I'm sure if I had to work on a step I'd be thinking ... why did they put this here of all places.She would like panel right over that step. easy to stand and work on and passes the 3x3x6 rule. Code ?
‘Steps’ is plural, this is only one step, and it’s not a stairway240.24(F)- overcurrent protective device not located over steps
While I wholeheartedly agree with you, the code states otherwise and is lacking the unique specificity of Cletus's subpanal, IMO.Stairway or step, I sure would hate having to stand with one foot on each level while working on it.
....240.24 states “....above the floor or working platform”, IMO, the floor is not a working platform , hence the mentioned distinction. I do agree with you that it should be one continuous, level floor space below the panels width.If it is a hall with a single level change & a typical interior panel then the maximum it needs to move horizontally would be 7" either way from the center of the panel - you may have the edge of the panel @ the edge corner of the step. 240.24 does say working platform which indicates a level flat surface. Tell your owner to get a life on such a trivial issue that could be unsafe for someone to examine live. Wait till their AFCI start tripping on kitchen appliances, this could be a lifetime job.
I agree.It has been almost 36 hours and the OP has not been back to provide any clarity on the installation.
I refuse to play a 'What If' guessing game.
Makes perfect sense. Good place to wrap things up.I would at least use the 30" width measurement, so that the floor under, and at least to one side of, the panel is flat.