I love following Charlie. Yeah, what he said.
Yea, that is important too. I have one client that insists that the feeder to any panel be sized for the full ampere rating of the panel, even if the intended (or calculated) load is lower. That is not an NEC requirement, but is within their published standards.And the feeders are sized to the load also,right?
And the feeders are sized to the load also,right?
Yea, that is important too. I have one client that insists that the feeder to any panel be sized for the full ampere rating of the panel, even if the intended (or calculated) load is lower. That is not an NEC requirement, but is within their published standards.
It's always been my thought that if you were putting in a 200 amp panel and the main can handle the load, why not? Same amount of work just bigger conduit and wire.
I guess I need to join-in by saying, ?what everyone else said.?
H
Yea, that is important too. I have one client that insists that the feeder to any panel be sized for the full ampere rating of the panel, even if the intended (or calculated) load is lower. That is not an NEC requirement, but is within their published standards.
I tryWell said.
That was stated in my client's standards.Are you saying it's within the panel's published standards that even if a feeder is properly protected with OCPD upstream it has to be sized to the panels full amp rating or are you talking about our client's standards?
That was stated in my client's standards.