Have been on here MANY times and always got god advice that passed inspection, now I am working on my own house, finally!
Sub panel in barn, not connect to house in any way, about 100' apart. PVC conduit from house main panel to barn sub panel, fed by 30 AMP double pole, 10-3, 2 hots, 1 neutral, ground not used.
At sub panel in barn , hots connected to lugs, neutral connected to lugs, and then a ground rod with #6 bare, not touching the sub panel box. I assume that the neutral wire and ground rod wire should not be connected in anyway in the sub panel, correct? I am under the impression that the ground rod at the sub panel is lightning protection ONLY and all faults will be cleared through the neutral back to the main panel in the house.
With that said, when I run my 20A breakers, do my neutral and ground terminate on the same bar in the sub panel?
Sub panel in barn, not connect to house in any way, about 100' apart. PVC conduit from house main panel to barn sub panel, fed by 30 AMP double pole, 10-3, 2 hots, 1 neutral, ground not used.
At sub panel in barn , hots connected to lugs, neutral connected to lugs, and then a ground rod with #6 bare, not touching the sub panel box. I assume that the neutral wire and ground rod wire should not be connected in anyway in the sub panel, correct? I am under the impression that the ground rod at the sub panel is lightning protection ONLY and all faults will be cleared through the neutral back to the main panel in the house.
With that said, when I run my 20A breakers, do my neutral and ground terminate on the same bar in the sub panel?