Greetings. I am installing three sub panels for a building that has two residential units and one commercial space. The service is 400amp. I'm trying to decide if a 125 amp panel is sufficient for each of the residential units. My calculations are listed below:
1500 Sq ft. x 3 is 4500 watts for general lighting.
2 appliance circuits = 3000 watts
1 laundry circuit 1500 watts
Total is 9000 watts
100% of first 3,000 plus 35% of the remaining 6000=
3000 + 2100 = 5,100 watts for Lighting ans small appliance load
1 Range, less than 12kv is derated to 8,000 watts.
There are 10, 1,000 watt baseboard heaters = 10,000 at 100%
Dryer 5,000
Water Heater 4,500
Dishwasher 1,440
Disposal 1440
Microwave 1440
total other loads is 13,820 @ 75% is 10,365
Total 33,465 divided by 240 is 139.43 amps.
So, I suppose 150 amp panel for each resi unit would squeak by.
Does my math look OK here?
Also, as far as calculating the entire service. Do I add the two resi units at 100% then do calcs on the commercial?
Thanks.
1500 Sq ft. x 3 is 4500 watts for general lighting.
2 appliance circuits = 3000 watts
1 laundry circuit 1500 watts
Total is 9000 watts
100% of first 3,000 plus 35% of the remaining 6000=
3000 + 2100 = 5,100 watts for Lighting ans small appliance load
1 Range, less than 12kv is derated to 8,000 watts.
There are 10, 1,000 watt baseboard heaters = 10,000 at 100%
Dryer 5,000
Water Heater 4,500
Dishwasher 1,440
Disposal 1440
Microwave 1440
total other loads is 13,820 @ 75% is 10,365
Total 33,465 divided by 240 is 139.43 amps.
So, I suppose 150 amp panel for each resi unit would squeak by.
Does my math look OK here?
Also, as far as calculating the entire service. Do I add the two resi units at 100% then do calcs on the commercial?
Thanks.