ajj73
Member
- Location
- Naperville, IL USA
I am planning on installing a sub panel from a 200 amp main panel in an attached garage where the requirement will be 90 amps max. I have available for FREE enough 4 AWG Copper cable to make the run and I am trying to understand the NEC as it applies to breaker sizing for a sub panel. The run is less than 40 feet long and will be installed in EMT. I am trying to determine the appropriate I am having trouble understanding what part of the code applies for proper sizing. My instinct says that I can use table Table 310-15(b)(6) and use a breaker of 100 amps in the main panel. However, then I read Table 310-16 and I begin to think I need that I will need to upgrade to 2 AWG copper. Can someone clarify this for me?