Sub Panel

Status
Not open for further replies.
Add a 100A sub panel to a 2 section 3 phase 120/208 panel that is full.

  1. Commercial installation / office building.
  2. Existing panel (section 1&2) is located in a parking garage electric room.
  3. New Sub Panel would be located in the same room as existing panels.
  4. New proposed sub panel type: 3p4w...208y/120v...100A...MLO...w/1-2p20 and 16-1p20 (18 ckt panel)
  5. Use 1-3p100 in LPA section 1 to feed new sub panel (relocate 3-1p20 receptacle ckt's to sub panel).
  6. Red is the proposed sub panel. View attachment 13097

I'm concerned that the sub panel would be to much for the existing panel to handle. I did what I think is a workaround if you don't know all the existing panel information. I just based everything existing off of 80% but I feel like I'm way off and a few things don't make sense to me. Below is the breakdown.


  • Existing panel (LPA section 1) has a 225A main and is a 42 ckt panel.
  • LPA section 1 has the following breakers. 1-3p225 Main, 25-1p20, 15-1p15, and 1-2p40
    • 20A*(25-1p breakers)*80%*120V = 48,000VA
    • 15A*(15-1p breakers)*80%*120V = 21,600VA
    • 40A*(1-2p breaker)*80%*208V = 6,656VA
    • Total = 76,256VA

  • Existing panel (LPA section 2) is MLO and is a 42 ckt panel.
  • LPA section 2 has the following breakers. 14-1p20, 12-2p30, and 2-2p40
    • 20A*(14-1p breakers)*80%*120V = 26,880VA
    • 30A*(12-2p breakers)*80%*208V = 59,904VA
    • 40A*(2-2p breakers)*80%*208V = 13,312VA
    • Total = 100,096VA

  • New Sub Panel.I was thinking to just use the 100A sub panel as the design load. Exactly what this will be used for is unknown.
    • 100A*80%*208*1.732*1.25 = 36,025VA

  • Total
    • 76,256VA + 100,096VA + 36,025VA = 212,377VA
    • 212,377VA / 208V / 1.732 = 589.51A

​With this total it doesn't look to me like there is any way I can add this panel? Am I even in the ballpark on this?
This brings me to my second question. If you take the LPA Section 1 total on its own it looks like a 225A main is correct but when you add LPA section 2 into the mix it doesn't seam to jive. On top of that LPA Section 2 alone looks more than a 225A Main can handle. I understand it was probably originally calculated at the demand load but with both panels together something doesn't look right.
Is there a solution for this?

LPA Section 1

  • 76,256VA / 208 / 1.732 = 211.67A
LPA Section 2
  • 100,096VA / 208 / 1.732 = 277.85A
Total
  • 211.67A + 277.85A = 489.52A
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Did you perform an actual load calculation based on the existing loads and Article 220?
 

iwire

Moderator
Staff member
Location
Massachusetts
I did what I think is a workaround if you don't know all the existing panel information. I just based everything existing off of 80% but I feel like I'm way off and a few things don't make sense to me.


Going by the handle rating minus 80% is meaningless. It really is, you would do as well by rolling a set of dice.

The only way to do this is per article 220.
 