It would depend on your AHJ and which building code you are under. Most inspectors here will allow that as long as there is no openings on the other side of the wall.
Your best bet would be to ask your AHJ or inspector.
 

rnatalie

Senior Member
Location
Catawba, NC
Occupation
Retired Electrical Engineer
The IRC requires a certain protection on the garage/residence wall and that it needs to be applied on the garage side. There are some exceptions for smaller (less than 16 sq in) electrical boxes, but not for panels. Wire penetrations are OK as long as they are property fireblocked. Most panels do not have a fire rating and can't be used as one.

You could surface mount it, or build out a new wall for it that's not part of the legal "membrane."
 

rnatalie

Senior Member
Location
Catawba, NC
Occupation
Retired Electrical Engineer
Square D specifically says theirs are not. I don't know about others, but I suspect not. 3M makes some matting that they claim is a listed way of protecting behind electrical panels. The IRC is somewhat silent on this technique.
 