Sub panel

Merry Christmas

Jmoney69

Member
Location
Detroit mi
Occupation
Apprentice
I have a 200A main panel in my house and want to put a 100A sub in pole barn. I have 2 spare 200A panels ML/MB. Am i ok to feed the 200A MB panel in pole barn from a 100A breaker in my house panel?

Thank you for your response!
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
Yes. you could supply a 600 amp panelboard from a 100 amp feeder and there is no code violation.

Supplying a 100 amp panelboard from a 600 amp feeder however all comes down to some details particularly related to feeder tap rules as to whether that is ok or not.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Yes, but the barn will need a disconnect, either outside or nearest inside.

A main breaker can be that disconnect if it meets the location requirements.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
I have a 200A main panel in my house and want to put a 100A sub in pole barn. I have 2 spare 200A panels ML/MB. Am i ok to feed the 200A MB panel in pole barn from a 100A breaker in my house panel?

Thank you for your response!
Yes; as long as the rating of the OCPD protecting the subpanel is equal to or less than the subpanel busbar rating, the bus rating in the sub is irrelevant.
 