finster1
Member
- Location
- New Jersey
I love all the hype subpanels create, but I've had this arguement before and I believe it is clear. If I was to run a subpanel in say a basement(indoors, for arguement sake) in conduit lets say 1" emt. The proper size wire for a 240v single phase 100A service would be (3) #3 thhn 2 HOTS A NEUTRAL and I prefer to run a seperate ground even though my hypothetical senario is emt and it is not necessary. I feel the seperate ground, ends the need for bonding bushings at the concentric fittings usually found at the panel knockouts. I mention all these things because I've sat around and argued with my collegues on almost all the things I've mentioned from concentric knockouts requiring a bonding bushing, to the size of the wire to actually be allowed for a 100 amp panel, to the need or lack of a ground if you are using emt. #3 thhn should clearly be the choice for 100....I see #4 all the time and technically I feel it shouldn't be allowed to be protected by a 100a breaker.Also another issue I have and I am not sure where it is addressed, can we use aluminum wiring for a subpanel in an indoor area.... Here in NJ the insurance companies really frown on aluminum except as a service wire for the main panel.....a sub is technically not that, so why do I find it installed even in recent applications indoors??? OK enuff said...any feelings guys?
Jim P
Licensed Electrical Contractor NJ
Jim P